by Forum Tech » Wed Nov 18, 2009 5:00 pm
"Neil,Sorry about the delay.There have been a couple of fans in the kits that are drawing too much current and causing the module to shut the compressor off. It sounds like you may have one of these fans.If you can get a LED and connect it to the module, it will give a series of flashes when a fault occurs. This will be helpful in troubleshooting this. I suspect that you will be seeing two flashes. The diode connects between the small "+" and "D" terminals on the control module. The diode polarity must be observed. When the compressor stops, there will be a series of flashes followed by a pause. The diagnostic codes are here:www.rparts.com/Catalog/Major_Components/compressors/Danfoss/BD50F_compressor.pdfAnother common reason for this to happen is low voltage at the control module. Check the voltage at the power connections at the module when the unit is trying to start, and assure that it doesn't drop below 10.4 volts.If it turns out to be the fan drawing too much current, we will replace the fan. The newer kits will have a different fan that draws slightly less current.A quick test is to disconnect the fan and try starting the system. If it starts and runs normally, then the fan is the problem. It's ok to run the system for a few minutes without the fan. Watch the high side, and stop the system if it gets much over 250 psig.Hope this helps, please let me know.Forum Tech"