by Forum Tech » Sat Jan 16, 2010 5:00 pm
"Brad,Check the wiring to assure that the fan circuit is connected between terminals 3 and 4 on the thermostat. The two terminals are at right angles to each other. There are two tabs labeled "4", and only one wire should attach to one of them. The other wire attaches to terminal 3.If it still doesn't work, 015-0284 might be a better choice. But the t'stat you have should work. Check the wiring, and maybe put it in the freezer so it gets cold enough to shut off.No, the t'stat body can be in the cold space, the probe and controller can be in the same area with no problem.Hope this helps,Forum Tech"